Which of the following options is/are correct for the Automatic Generation Control (AGC) and Automatic Voltage Regulator (AVR) installed with synchronous generators?
AGC response has a local effect on frequency while AVR response has a global effect on voltage.
AGC response has a global effect on frequency while AVR response has a local effect on voltage.
AGC regulates the field current of the synchronous generator while AVR regulates the generator’s mechanical power input.
AGC regulates the generator’s mechanical power input while AVR regulates the field current of the synchronous generator.
Correct answer: (B) AGC response has a global effect on frequency while AVR response has a local effect on voltage.; (D) AGC regulates the generator’s mechanical power input while AVR regulates the field current of the synchronous generator.
Explanation
Frequency is common to the whole interconnected system, so the AGC (load-frequency control) has a global effect, whereas voltage is a local quantity, so the AVR acts locally. AGC adjusts the prime mover's mechanical power input (governor set point), while the AVR adjusts the exciter and hence the field current.
More Voltage and Frequency control, Power factor correction questions
GATE 2022 EE Q56– Two generating units rated for 250 MW and 400 MW have governor regulations of 6% and 6.4%,…
GATE 2020 EE Q33– A single 50 Hz synchronous generator on droop control was delivering 100 MW power to a…
GATE 2020 EE Q56– A cylindrical rotor synchronous generator with constant real power output and constant…
GATE 2016 EE Q50– A three-phase cable is supplying 800 kW and 600 kVAr to an inductive load. It is intended…
GATE 2017 EE Q49– A load is supplied by a 230 V, 50 Hz source. The active power P and the reactive power Q…
GATE 2014 EE (EE2) Q24– A single-phase induction motor draws 12 MW at 0.6 lagging power factor. A parallel…