Thermodynamics (XE4) · Second Law of Thermodynamics · 1 mark · Numerical answer

A house loses heat at 150 MJ per hour. Outside temperature is −3°C and the required inside temperature is 25°C. Find the minimum heat-pump power in kW, to two decimals.

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: 3.70 to 4.20

Explanation

The minimum input corresponds to a reversible heat pump. The temperature lift is 298.15 − 270.15 = 28 K, so COPmax = TH/(TH−TC) = 298.15/28. The heating load is 150,000/3600=41.6667 kW. Therefore Wmin = QH/COPmax = 41.6667 × 28/298.15 ≈ 3.9130 kW, or 3.91 kW. Absolute temperatures must be used in the COP.