GATE 2026 XE — all source sections – Question 105
Moist air enters an adiabatic saturator at 45°C and 101 kPa and leaves saturated at 30°C. Make-up water enters at 30°C. Find make-up water in grams per kg of dry air, to two decimals. Use cp, water=4.2 and cp, dry air=1 kJ kg⁻¹ K⁻¹. Saturated properties: at 30°C, hg=2556 kJ/kg, hf=125.7 kJ/kg, Psat=4.25 kPa; at 45°C, hg=2582 kJ/kg, hf=188.4 kJ/kg, Psat=9.60 kPa. (The source misprints enthalpy units with an extra K⁻¹.)
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: 6.30 to 6.60
Explanation
Outlet humidity ratio is ω₂=0.622×4.25/(101−4.25)=0.027322… kg/kg dry air. Let x=ω₂−ω₁ be make-up water per kg dry air. The energy balance is 45+ω₁×2582+x×125.7=30+ω₂×2556. Substitute ω₁=ω₂−x: x=(15+26ω₂)/(2582−125.7)=0.00639596 kg/kg. Therefore make-up is 6.40 g/kg dry air. Humidity ratio is based on dry-air mass, not total moist-air mass.