GATE 2018 XE — all source sections – Question 17
Moist air having 60% relative humidity, enters a steady-flow air-conditioning unit at 102 kPa
and 30 °C. The volume flow rate of the moist air entering the unit is 0.1 m3/s. The moist air
leaves the unit at 95 kPa and 15 °C with a relative humidity of 100%. Liquid condensate
leaves the unit at 15 °C.
For water: at 15 °C, ℎ𝑓 = 62.982 kJ/kg, ℎ𝑔 = 2528.3 kJ/kg, 𝑃𝑠𝑎𝑡 = 1.7057 kPa.
at 30 °C, ℎ𝑓 = 125.74 kJ/kg, ℎ𝑔 = 2555.6 kJ/kg, 𝑃𝑠𝑎𝑡 = 4.2469 kPa.
For air, specific heat at constant pressure is 1.004 kJ/kg.K and the specific gas constant is
0.287 kJ/kg.K.
Neglecting heat leakage to the surrounding, the magnitude of heat extracted (in kW) from
the air stream (up to 2 decimal places) is __________.
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: 3.01 to 3.07
Explanation
We are sorry we couldn't write detailed soluition for this, we are working on it!, please consider asking your own AI, its just 2-3 clicks with very minimum effort