A 10-bus power system consists of four generator buses indexed as G1, G2, G3, G4 and six load buses indexed as L1, L2, L3, L4, L5, L6. The generator-bus G1 is considered as slack bus, and the load buses L3 and L4 are voltage controlled buses. The generator at bus G2 cannot supply the required reactive power demand, and hence it is operating at its maximum reactive power limit. The number of non-linear equations required for solving the load flow problem using Newton-Raphson method in polar form is ________.
The slack bus G1 needs no equation. The voltage-controlled buses are G3, G4, L3 and L4 (4 buses), where the real power equation is needed. Bus G2 is at its reactive limit, so it behaves as a load bus. The load buses are L1, L2, L5, L6 and G2 (5 buses), which need both real and reactive power equations. The number of equations is $9 + 5 = 14$.
More Per-unit quantities, Bus admittance matrix, Gauss-Seidel and Newton-Raphson load flow methods questions
GATE 2017 EE Q50– The bus admittance matrix for a power system network is bmatrix -j39.9 & j20 & j20 \\ j20…
GATE 2014 EE (EE1) Q51– The two-bus system shown supplies load 1.0 + j0.5 pu. Find V₁ (pu) and δ₂ respectively.
GATE 2014 EE (EE2) Q25– A three-phase star load operates at 0.9 pu voltage and 0.8 lagging power factor. Base…
GATE 2017 EE (EE2) Q25– The figure is a per-phase phase-shifting transformer between buses 1 and 2, with complex…
GATE 2017 EE (EE2) Q35– A polar-coordinate Newton–Raphson load-flow problem has a 100×100 Jacobian and 20 PV…
GATE 2016 EE (EE2) Q24– A power system has 100 buses, including 10 generator buses. With polar-coordinate…