The series reactance $0.05$ pu has admittance $-j20$, and each end also has a shunt susceptance of $j0.05$. The line contributed $-j20 + j0.05 = -j19.95$ to each of the diagonal elements $Y_{11}$ and $Y_{33}$, and $+j20$ to $Y_{13}$ and $Y_{31}$. Removing the line adds $+j19.95$ to the diagonals, giving $-j39.9 + j19.95 = -j19.95$, and takes $Y_{13} = Y_{31}$ to 0.