GATE 2024 CE (CE1) – Question 50
An inverted T-shaped concrete beam (B1) in the figure, with centroidal axis X − X, is subjected to an effective prestressing force of 1000 kN acting at the bottom kern point of the beam cross-section. Also consider an identical concrete beam (B2) with the same grade of concrete but without any prestressing force.
The additional cracking moment (in kN.m) that can be carried by beam B1 in comparison to beam B2 is ____________ (rounded off to the nearest integer).

Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: 300
Explanation
The prestress $P$ acts at the eccentricity $e = 100$ mm below the centroid (the bottom kern point). It produces the compressive stress at the bottom fibre $\frac{P}{A} + \frac{Pe}{Z_b}$, and the extra moment the beam can carry before the bottom fibre cracks is $\Delta M = Z_b\left(\frac{P}{A} + \frac{Pe}{Z_b}\right) = P\left(\frac{Z_b}{A} + e\right)$. The bottom kern distance is $k_b = \frac{Z_t}{A} = 100$ mm. Since $Z = \frac{I}{y}$ and $y_t = \frac{2H}{3}$, $y_b = \frac{H}{3}$, we have $\frac{Z_b}{Z_t} = \frac{y_t}{y_b} = 2$, so $\frac{Z_b}{A} = 200$ mm. Therefore $\Delta M = 1000 \times (0.2 + 0.1) = 300$ kN m.