GATE 2023 CH – Question 45
Level ($h$) in a steam boiler is controlled by manipulating the flow rate ($F$) of the make-up (fresh) water using a proportional (P) controller. The transfer function between the output and the manipulated input is $\frac{h(s)}{F(s)} = \frac{0.25(1 - s)}{s(2s + 1)}$. The measurement and valve transfer functions are both equal to 1. A process engineer wants to tune the controller so that the closed-loop response gives decaying oscillations under servo mode. Which one of the following is the CORRECT value of the controller gain to be used by the engineer?
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: (B) 2
Explanation
The closed-loop characteristic equation is $1 + K_c\frac{0.25(1 - s)}{s(2s + 1)} = 0$, that is $2s^2 + (1 - 0.25K_c)s + 0.25K_c = 0$. For stability, $K_c < 4$. For complex roots (oscillation), the discriminant $(1 - 0.25K_c)^2 - 2K_c < 0$, which gives $K_c^2 - 40K_c + 16 < 0$ and so $0.4 < K_c < 39.6$. So decaying oscillations need $0.4 < K_c < 4$, and only $K_c = 2$ is in this range. ($K_c = 4$ gives sustained oscillation, 6 is unstable and 0.25 is overdamped.)