A square footing is to be designed to carry a column load of 500 kN which is resting on a soil stratum having the following average properties: bulk unit weight = 19 kN/m$^3$; angle of internal friction = 0° and cohesion = 25 kPa. Considering the depth of the footing as 1 m and adopting Meyerhof’s bearing capacity theory with a factor of safety of 3, the width of the footing (in m) is ______ (round off to one decimal place). [Assume the applicable shape and depth factor values as unity; ground water level at greater depth.]

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: 3.0 to 3.5

Explanation

For $\phi=0$, Meyerhof gives $N_c=\pi+2=5.14$, $N_q=1$, and $N_\gamma=0$. Net ultimate capacity is $25(5.14)=128.5$ kPa. With safety factor 3 the net safe pressure is 42.83 kPa. Size the area for the column load using this net pressure: $B=\sqrt{500/42.83}=3.42$ m, or 3.4 m. Adding overburden to the safe pressure while retaining the unreduced column pressure gave the former undersized footing.