GATE 2014 EE (EE1) – Question 46

Electrical Machines · Types of losses and efficiency calculations of electric machines · 2 marks · Multiple choice

The core loss of a single-phase 230/115 V, 50 Hz transformer is measured from the 230 V side with secondary open, using a variable-voltage, variable-frequency source. Loss is 1050 W at 230 V, 50 Hz and 500 W at 138 V, 30 Hz. Find hysteresis and eddy-current losses respectively at 230 V, 50 Hz.

  1. 508 W and 542 W
  2. 468 W and 582 W
  3. 498 W and 552 W
  4. 488 W and 562 W

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: (A) 508 W and 542 W

Explanation