GATE 2014 EE (EE1) – Question 46
The core loss of a single-phase 230/115 V, 50 Hz transformer is measured from the 230 V side with secondary open, using a variable-voltage, variable-frequency source. Loss is 1050 W at 230 V, 50 Hz and 500 W at 138 V, 30 Hz. Find hysteresis and eddy-current losses respectively at 230 V, 50 Hz.
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: (A) 508 W and 542 W
Explanation
Both tests have identical V/f:230/50=138/30, so peak flux is unchanged. Hysteresis loss scales as f, while eddy loss scales as f². Let H+E=1050at50Hz; at30Hz,0.6H+0.36E=500. Solving gives H=508.333Wand E=541.667W, matching **508Wand542W,A**.