A 3-phase, 11 kV, 10 MVA synchronous generator is connected to an inductive load of power factor $(\sqrt3/2)$ via a lossless line with a per-phase inductive reactance of 5 Ω. The per-phase synchronous reactance of the generator is 30 Ω with negligible armature resistance. If the generator is producing the rated current at the rated voltage, then the power factor at the terminal of the generator is
Rated phase voltage $V_t=11000/\sqrt3=6351$ V and rated current $I=\dfrac{10\times10^6}{\sqrt3\times11000}=524.9$ A. Take $I$ as reference and let the load voltage be $V_L\angle30^\circ$ (lagging load, pf 0.866). Then $V_t=V_L\angle30^\circ+j5I=0.866V_L+j(0.5V_L+2624)$. Setting $|V_t|=6351$: $V_L^2+2624V_L-3.345\times10^7=0$, so $V_L=4618$ V. Then $V_t=3999+j4933$, whose angle relative to $I$ is $51^\circ$, so the terminal power factor is $\cos51^\circ=0.63$ lagging. (The synchronous reactance does not affect this.)