GATE 2018 EE – Question 38
The positive, negative and zero sequence impedances of a three phase generator are $Z_1$, $Z_2$ and $Z_0$ respectively. For a line-to-line fault with fault impedance $Z_f$, the fault current is $I_{f1}=kI_f$, where $I_f$ is the fault current with zero fault impedance. The relation between $Z_f$ and $k$ is
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: (A) $Z_f=\dfrac{(Z_1+Z_2)(1-k)}{k}$
Explanation
For a line-to-line fault the fault current is proportional to $\frac{1}{Z_1+Z_2+Z_f}$, and for $Z_f=0$ it is proportional to $\frac{1}{Z_1+Z_2}$. So $k=\frac{Z_1+Z_2}{Z_1+Z_2+Z_f}$, which gives $Z_f=\frac{(Z_1+Z_2)(1-k)}{k}$.