A 3-bus power system is shown in the figure below, where the diagonal elements of $Y$-bus matrix are: $Y_{11} = -j12$ pu, $Y_{22} = -j15$ pu and $Y_{33} = -j7$ pu.
The per unit values of the line reactances $p$, $q$ and $r$ shown in the figure are
Each diagonal element is the sum of the admittances of the lines at that bus, and a line of reactance $x$ has admittance $-j/x$. So $\frac{1}{q} + \frac{1}{r} = 12$, $\frac{1}{q} + \frac{1}{p} = 15$ and $\frac{1}{p} + \frac{1}{r} = 7$. Adding gives $\frac{1}{p} + \frac{1}{q} + \frac{1}{r} = 17$, so $\frac{1}{p} = 5$, $\frac{1}{r} = 2$ and $\frac{1}{q} = 10$. That gives $p = 0.2$, $q = 0.1$ and $r = 0.5$.