The GATE Grind

GATE 2023 CH – Question 25

Instrumentation and Process Control · Process modelling, transfer functions and dynamic response · 1 mark · Multiple choice

A liquid surge tank has $F_{in}$ and $F_{out}$ as the inlet and outlet flow rates respectively, as shown in the figure below. $F_{out}$ is proportional to the square root of the liquid level $h$. The cross-sectional area of the tank is 20 cm$^2$. Density of the liquid is constant everywhere in the system. At steady state, $F_{in} = F_{out} = 10$ cm$^3$s$^{-1}$ and $h = 16$ cm. The variation of $h$ with $F_{in}$ is approximated as a first order transfer function. Which one of the following is the CORRECT value of the time constant (in seconds) of this system?

Diagram for GATE 2023 CH question 25
  1. 20
  2. 32
  3. 64
  4. 128

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: (C) 64

Explanation

Write $F_{out} = k\sqrt{h}$, with $k = \frac{10}{\sqrt{16}} = 2.5$. The balance is $A\frac{dh}{dt} = F_{in} - k\sqrt{h}$. Linearising about the steady state, $A\frac{dh'}{dt} = F_{in}' - \frac{k}{2\sqrt{\bar{h}}}h'$, and $\frac{k}{2\sqrt{\bar{h}}} = \frac{2.5}{8} = 0.3125$ cm²/s. The time constant is $\tau = \frac{A}{0.3125} = \frac{20}{0.3125} = 64$ s.