The GATE Grind

GATE 2022 CH – Question 22

Instrumentation and Process Control · Controller modes, control valves and tuning · 1 mark · Multiple choice

Liquid flowing through a heat exchanger (HX) is heated. A bypass stream is provided to control the temperature of the heated exit stream. From the given plumbing options, the one that provides the most effective temperature control for large disturbances while avoiding vaporization in the heat exchanger is

Diagram for GATE 2022 CH question 22
  1. Option A in the figure
  2. Option B in the figure
  3. Option C in the figure
  4. Option D in the figure

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: (C) Option C in the figure

Explanation

Effective control needs valves in both branches, so that the flow can be split between the exchanger and the bypass. To avoid vaporisation in the exchanger, its pressure must stay high, so the valve in the exchanger branch has to be on the outlet side of the exchanger. Layout C has this, and it also has the bypass valve. In D the valve is after the two streams join, so it does not split the flow, and in A and B the valve is upstream of the exchanger and lowers its pressure.

Official GATE 2022 answer key: https://gate2026.iitg.ac.in/doc/download/Answer_keys2022/ch_2022.pdf

More Controller modes, control valves and tuning questions

All Controller modes, control valves and tuning questions →