A 230 V rms source feeds two parallel loads: 10 kW at 0.8 leading power factor, and 10 kVA at 0.8 lagging power factor. Find complex power delivered by the source.
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: (B) (18 − j1.5) kVA
Explanation
The first load has P1=10kW and leading power factor0.8, so Q1=−P1tan(arccos0.8)=−7.5kVAr. The second has apparent power10kVA at lagging0.8, giving P2=8kW and Q2=6kVAr. Add complex powers: S=18−j1.5kVA, **B**. Leading reactive power is negative.