The figure shows the single-line diagram of a synchronous generator delivering $P=50$ MW of power at unity power factor to an infinite bus.
$\bar I_s$ denotes the stator current phasor. If the field excitation is increased, which one of the following options correctly describes its effect on the stator current, power factor, and load angle of the machine?
Stator current increases, power factor becomes lagging, load angle remains the same
Stator current decreases, power factor becomes leading, load angle remains the same
Stator current increases, power factor becomes lagging, load angle decreases
Stator current increases, power factor becomes leading, load angle increases
Correct answer: (C) Stator current increases, power factor becomes lagging, load angle decreases
Explanation
The real power stays 50 MW. Raising the excitation ($E_f$) makes the machine over-excited, so it supplies reactive power: the current gets a lagging component, the stator current magnitude rises and the power factor becomes lagging. Since $P\propto E_fV\sin\delta$ is constant, a larger $E_f$ means a smaller $\sin\delta$: the load angle decreases.
More Synchronous machines: cylindrical and salient pole machines, performance and characteristics, regulation and parallel operation of generators, starting of synchronous motors questions
GATE 2025 EE Q35– The induced emf in a 3.3 kV, 4 pole, 3-phase star connected synchronous motor is…
GATE 2024 EE Q40– A 3-phase, 11 kV, 10 MVA synchronous generator is connected to an inductive load of power…
GATE 2023 EE Q22– The four stator conductors (A, A′, B and B′) of a rotating machine are carrying DC…
GATE 2023 EE Q47– A three-phase synchronous motor with synchronous impedance of 0.1+j0.3 per unit per phase…
GATE 2022 EE Q64– A star-connected 3-phase, 400 V, 50 kVA, 50 Hz synchronous motor has a synchronous…
GATE 2021 EE Q18– Consider the table given: Constructional feature Machine type Mitigation --- --- --- (P)…