For the three-bus power system shown in the figure, the trip signals to the circuit breakers $B_1$ to $B_9$ are provided by overcurrent relays $R_1$ to $R_9$, respectively, some of which have directional properties also. The necessary condition for the system to be protected for short circuit fault at any part of the system between bus 1 and the R-L loads with isolation of minimum portion of the network using minimum number of directional relays is
$R_3$ and $R_4$ are directional overcurrent relays blocking faults towards bus 2
$R_3$ and $R_4$ are directional overcurrent relays blocking faults towards bus 2 and $R_7$ is directional overcurrent relay blocking faults towards bus 3
$R_3$ and $R_4$ are directional overcurrent relays blocking faults towards Line 1 and Line 2, respectively, $R_7$ is directional overcurrent relay blocking faults towards Line 3 and $R_5$ is directional overcurrent relay blocking faults towards bus 2
$R_3$ and $R_4$ are directional overcurrent relays blocking faults towards Line 1 and Line 2, respectively.
Correct answer: (A) $R_3$ and $R_4$ are directional overcurrent relays blocking faults towards bus 2
Explanation
Lines 1 and 2 are in parallel between buses 1 and 2. For a fault on one of them, the healthy line can feed the fault from bus 2 through its bus-2 breaker. Directional relays $R_3$ and $R_4$ at the bus-2 ends of the two lines block current flowing back toward bus 1 from bus 2, so only the faulty line trips. Line 3 is radial (it has a single source), so it needs no directional relays.
More Principles of over-current, differential, directional and distance protection; Circuit breakers questions
GATE 2022 EE Q13– The most commonly used relay, for the protection of an alternator against loss of…
GATE 2020 EE Q18– A lossless transmission line with 0.2 pu reactance per phase uniformly distributed along…
GATE 2019 EE Q62– In a 132 kV system, the series inductance up to the point of circuit breaker location is…
GATE 2014 EE (EE1) Q25– A three-phase-to-ground fault occurs at F₁ or F₂ in the system shown. Bus-A voltages and…
GATE 2014 EE (EE1) Q53– IDMT line-protection relays and loads are shown. Their characteristic is t…
GATE 2016 EE (EE2) Q23– The shown two-generator system has six overcurrent relays R1–R6, using an appropriate mix…