A lossless transmission line with 0.2 pu reactance per phase uniformly distributed along the length of the line, connecting a generator bus to a load bus, is protected up to 80% of its length by a distance relay placed at the generator bus. The generator terminal voltage is 1 pu. There is no generation at the load bus. The threshold pu current for operation of the distance relay for a solid three phase-to-ground fault on the transmission line is closest to:
The relay must operate for a fault at 80% of the line, i.e. at a reactance of $0.8\times0.2=0.16$ pu from the relay. With 1 pu voltage and no other source, the fault current is $\frac{1}{0.16}=6.25$ pu.