A three-phase cylindrical rotor synchronous generator has a synchronous reactance $X_s$ and a negligible armature resistance. The magnitude of per phase terminal voltage is $V_A$ and the magnitude of per phase induced emf is $E_A$. Considering the following two statements, P and Q,
P: For any three-phase balanced leading load connected across the terminals of this synchronous generator, $V_A$ is always more than $E_A$.
Q: For any three-phase balanced lagging load connected across the terminals of this synchronous generator, $V_A$ is always less than $E_A$.
With a lagging load the armature reaction is demagnetizing, so $V_A<E_A$ always (Q is true). For a leading load $V_A$ exceeds $E_A$ only when the load is sufficiently leading; a load at unity power factor, or slightly leading, still gives $V_A<E_A$. So P is false.