GATE 2016 EE (EE2) – Question 48

Power Systems · System stability concepts, Equal area criterion · 2 marks · Numerical answer

The balanced system has generator internal and infinite-bus voltages fixed at 1 pu. Component reactances are shown. A three-phase fault occurs midway along line 2. The ratio of pre-fault to faulted maximum transferable real power is ________.

Diagram for GATE 2016 EE (EE2) question 48

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: 2.20 to 2.35

Explanation

Before the fault, the two transformer-plus-line branches each have reactance 0.1+0.5=0.6 pu. In parallel they give 0.3, and with generator reactance 0.2 the transfer reactance is 0.5 pu.

During the fault the healthy path remains 0.6, while the sending junction has shunt reactance 0.1+0.25=0.35 to the fault. Eliminating that junction gives effective transfer reactance $0.2+0.6+(0.2\cdot0.6)/0.35=1.142857$ pu.

Since Pmax=EV/Xtransfer, the requested ratio is 1.142857/0.5=**2.28571**, in 2.20–2.35.