GATE 2016 EE (EE2) – Question 61
Three single-phase transformers form a 110 kV/11 kV delta–star bank delivering 8 MW at 0.8 lagging pf at 11 kV. Neglect losses. The ratio of delta-side phase current to star-side phase current is
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: (A) $1:10\sqrt3$
Explanation
The line-voltage ratio is 10, so line currents have inverse ratio 1:10. In delta, phase current equals line current divided by √3; in star, phase and line currents are equal.
Therefore IΔ,phase/IY,phase=(1/10)/√3. The ratio is **1:10√3, A**. The load magnitude and pf cancel in this ratio.
More Three-phase transformers: connections, vector groups, parallel operation questions
- GATE 2015 EE (EE2) Q53
- GATE 2015 EE (EE2) Q61
- GATE 2026 EE Q38
- GATE 2025 EE Q43
- GATE 2020 EE Q58
- GATE 2018 EE Q61
All Three-phase transformers: connections, vector groups, parallel operation questions →