GATE 2015 EE (EE2) – Question 61
The two three-phase transformer banks are built from single-phase units with the shown winding polarities. Find the phase-difference magnitude between V1 and V2 in degrees.

Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: 30
Explanation
Both banks have the same primary delta connection. The upper secondary is delta, so V1 follows a secondary winding voltage. The lower secondary is star, so V2 is the difference of two phase winding voltages.
For a balanced sequence, the difference of equal phasors separated by 120° has √3 times the magnitude and a 30° displacement. The shown polarities therefore give an inter-bank line-voltage phase difference of **30°**.
More Three-phase transformers: connections, vector groups, parallel operation questions
- GATE 2026 EE Q38
- GATE 2025 EE Q43
- GATE 2020 EE Q58
- GATE 2018 EE Q61
- GATE 2016 EE Q52
- GATE 2015 EE Q61
All Three-phase transformers: connections, vector groups, parallel operation questions →