A 220 V,three-phase,four-pole,50 Hz wound-rotor induction motor has negligible stator resistance, magnetizing reactance and core loss. Maximum torque is 225% of full-load torque at slip 0.15. Actual rotor resistance is 0.03 Ω/phase. Find added rotor resistance for maximum torque at starting.
With negligible stator resistance, maximum-torque slip is proportional to total rotor resistance: sm=R2/Xeq on a consistent rotor basis.
Initially 0.15=0.03/Xeq, giving Xeq=0.2 Ω. To make sm=1, total resistance must become 0.2 Ω.
The external addition is 0.2−0.03=**0.17 Ω per rotor phase**, within 0.16–0.18. The maximum-torque magnitude ratio is not needed for this shift.