Two identical unloaded generators are paralleled as shown. Each has positive-, negative- and zero-sequence impedances j0.4,j0.3,j0.15 pu. Prefault voltage is 1 pu. Find line-to-ground terminal fault current in pu.

Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: 5.5 to 6.5
Explanation
Positive-sequence sources are paralleled, giving Z1=j0.4/2=j0.2. Negative-sequence impedances likewise give Z2=j0.15.
Only the generator with grounded neutral supplies zero-sequence current; the ungrounded star blocks it. Thus Z0=j0.15, rather than half that value.
For a solid single-line-ground fault, $|I_f|=|3V/(Z_1+Z_2+Z_0)|=3/0.5=$ **6 pu**.