GATE 2023 XE — all source sections – Question 105
A refrigerator operates on an ideal vapor compression cycle between the pressure limits of 140 kPa and 800 kPa. The working fluid is the refrigerant R-134a. The refrigerant enters the compressor as saturated vapor at 140 kPa and exits at 800 kPa and 60 ℃. It leaves the condenser as a saturated liquid at 800 kPa. The coefficient of performance (COP) of the refrigerator is ____________ (rounded off to two decimal places). Use the following property data for R-134a: At 140 kPa: hf = 27.06 kJ/kg, hg = 239.19 kJ/kg At 800 kPa: hf = 95.48 kJ/kg, hg = 267.34 kJ/kg At 800 kPa and 60 ℃: h = 296.82 kJ/kg
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: 2.45 to 2.55
Explanation
Refrigerating effect is h1 − h3 = 239.19 − 95.48 = 143.71 kJ/kg, using isenthalpic throttling. Compressor work is h2 − h1 = 296.82 − 239.19 = 57.63 kJ/kg. COP = 143.71/57.63≈2.49. Condenser-exit saturated-liquid enthalpy is the throttle-inlet value.