A single-phase transformer of rating 25 kVA, supplies a 12 kW load at power factor of 0.6 lagging. The additional load at unity power factor in kW (round off to two decimal places) that may be added before this transformer exceeds its rated kVA is ________.
The present load is $S=\frac{12}{0.6}=20$ kVA with $Q=\sqrt{20^2-12^2}=16$ kvar. Adding $P$ kW at unity power factor, $\sqrt{(12+P)^2+16^2}=25$ gives $12+P=19.2$, so $P=7.2$ kW.