Electrical Machines · Single phase transformer: equivalent circuit, phasor diagram, open circuit and short circuit tests, regulation and efficiency · 1 mark · Multiple choice

A single-phase 100 kVA, 1000 V / 100 V, 50 Hz transformer has a voltage drop of 5% across its series impedance at full load. Of this, 3% is due to resistance. The percentage regulation of the transformer at full load with 0.8 lagging power factor is

  1. 4.8
  2. 6.8
  3. 8.8
  4. 10.8

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: (A) 4.8

Explanation

Percentage resistance drop $=3\%$ and total impedance drop $=5\%$, so the percentage reactance is $\%X=\sqrt{5^2-3^2}=4\%$.

Regulation at full load $=\%R\cos\phi+\%X\sin\phi$. With $\cos\phi=0.8$ lagging, $\sin\phi=0.6$:

$3(0.8)+4(0.6)=2.4+2.4=4.8\%$.