A single-phase 100 kVA, 1000 V / 100 V, 50 Hz transformer has a voltage drop of 5% across its series impedance at full load. Of this, 3% is due to resistance. The percentage regulation of the transformer at full load with 0.8 lagging power factor is
4.8 6.8 8.8 10.8 Practise this question in The GATE Grind →
Show answer and explanation Correct answer: (A) 4.8
Explanation Percentage resistance drop $=3\%$ and total impedance drop $=5\%$, so the percentage reactance is $\%X=\sqrt{5^2-3^2}=4\%$.
Regulation at full load $=\%R\cos\phi+\%X\sin\phi$. With $\cos\phi=0.8$ lagging, $\sin\phi=0.6$:
$3(0.8)+4(0.6)=2.4+2.4=4.8\%$.
More Single phase transformer: equivalent circuit, phasor diagram, open circuit and short circuit tests, regulation and efficiency questions GATE 2016 EE Q35 – If an ideal transformer has an inductive load element at port 2 as shown in the figure… GATE 2015 EE Q32 – The self inductance of the primary winding of a single phase, 50 Hz, transformer is 800… GATE 2014 EE (EE1) Q22 – At specified transformer input voltage and frequency, the equivalent core radius is… GATE 2016 EE (EE2) Q13 – An ideal transformer has primary:secondary turns 1:100. The primary is driven by 100 V… GATE 2015 EE (EE2) Q30 – Choose transformer ratios a,b so Zin is purely resistive and equals 2.5 Ω at angular… GATE 2015 EE (EE2) Q57 – A three-winding transformer has N1=100,N2=N3=50 and negligible magnetizing current. With… All Single phase transformer: equivalent circuit, phasor diagram, open circuit and short circuit tests, regulation and efficiency questions →