Home › Previous year questions › GATE 2015 EE (EE2) › Question 57GATE 2015 EE (EE2) – Question 57 Electrical Machines · Single phase transformer: equivalent circuit, phasor diagram, open circuit and short circuit tests, regulation and efficiency · 2 marks · Multiple choice
A three-winding transformer has N1=100,N2=N3=50 and negligible magnetizing current. With the shown polarities, $\bar I_2=2\angle30^\circ$ A and $\bar I_3=2\angle150^\circ$ A. Primary I1 is
$1\angle90^\circ$ A $1\angle270^\circ$ A $4\angle90^\circ$ A $4\angle270^\circ$ A Practise this question in The GATE Grind →
Show answer and explanation Correct answer: (A) $1\angle90^\circ$ A
Explanation The primary current enters its dotted terminal, while both load currents leave their dotted terminals. Ampere-turn balance gives N1I1=N2I2+N3I3.
Therefore I1=(I2+I3)/2. The two load phasors add to 2j A because their real components cancel and their imaginary components each equal 1 A.
Thus I1=j A=**1∠90° A, A**.
More Single phase transformer: equivalent circuit, phasor diagram, open circuit and short circuit tests, regulation and efficiency questions GATE 2026 EE Q31 – A 220 V/12 V single-phase transformer is designed for use in India and rated 100 VA at 50… GATE 2024 EE Q18 – Which one of the following options represents possible voltage polarities in a single… GATE 2023 EE Q53 – When the winding c-d of the single-phase, 50 Hz, two winding transformer is supplied from… GATE 2021 EE Q43 – In a single-phase transformer, the total iron loss is 2500 W at nominal voltage of 440 V… GATE 2020 EE Q31 – A single-phase, 4 kVA, 200 V/100 V, 50 Hz transformer with laminated CRGO steel core has… GATE 2019 EE Q18 – A 5 kVA, 50 V/100 V, single-phase transformer has a secondary terminal voltage of 95 V… All Single phase transformer: equivalent circuit, phasor diagram, open circuit and short circuit tests, regulation and efficiency questions →