A 220 V/12 V single-phase transformer is designed for use in India and rated 100 VA at 50 Hz. Later, this unit is shipped to the USA where it is used as a 110 V/6 V transformer at 60 Hz.
Which of the following statements is/are correct?
No-load current drawn would be smaller for operation in the USA compared to that in India
For the same load current, the losses would be higher in the USA compared to that in India
The peak magnetic flux density in the core would be higher while operating in the USA compared to that in India
The eddy current losses in the core would be approximately 44% higher while operating in the USA compared to that in India
Correct answer: (A) No-load current drawn would be smaller for operation in the USA compared to that in India
Explanation
The peak flux is $\phi_m\propto V/f$: $\dfrac{110/60}{220/50}=0.417$, i.e. it drops to about 42% (C is false). A lower flux means a smaller magnetising (no-load) current: A is true. Copper losses depend on the load current, which is the same, so the losses are not higher (B false). Eddy-current loss scales as $B_m^2f^2\propto V^2$, so it is $(110/220)^2=0.25$ of the original, not 44% higher (D false).
More Single phase transformer: equivalent circuit, phasor diagram, open circuit and short circuit tests, regulation and efficiency questions
GATE 2024 EE Q18– Which one of the following options represents possible voltage polarities in a single…
GATE 2023 EE Q53– When the winding c-d of the single-phase, 50 Hz, two winding transformer is supplied from…
GATE 2021 EE Q43– In a single-phase transformer, the total iron loss is 2500 W at nominal voltage of 440 V…
GATE 2020 EE Q31– A single-phase, 4 kVA, 200 V/100 V, 50 Hz transformer with laminated CRGO steel core has…
GATE 2019 EE Q18– A 5 kVA, 50 V/100 V, single-phase transformer has a secondary terminal voltage of 95 V…
GATE 2019 EE Q55– A single-phase transformer of rating 25 kVA, supplies a 12 kW load at power factor of 0.6…