A 220 V/12 V single-phase transformer is designed for use in India and rated 100 VA at 50 Hz. Later, this unit is shipped to the USA where it is used as a 110 V/6 V transformer at 60 Hz.
Which of the following statements is/are correct?
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: (A) No-load current drawn would be smaller for operation in the USA compared to that in India
Explanation
The peak flux is $\phi_m\propto V/f$: $\dfrac{110/60}{220/50}=0.417$, i.e. it drops to about 42% (C is false). A lower flux means a smaller magnetising (no-load) current: A is true. Copper losses depend on the load current, which is the same, so the losses are not higher (B false). Eddy-current loss scales as $B_m^2f^2\propto V^2$, so it is $(110/220)^2=0.25$ of the original, not 44% higher (D false).