Instrumentation and Process Control · Controller modes, control valves and tuning · 1 mark · Multiple choice

Consider the control structure for the overhead section of a distillation column shown in the figure. The composition controller (CC) controls the heavy key impurity in the distillate by adjusting the setpoint of the reflux flow controller in a cascade arrangement. The sign of the controller gain for the pressure controller (PC) and that for the composition controller (CC) are, respectively,

Diagram for GATE 2024 CH question 23
  1. negative, negative
  2. negative, positive
  3. positive, positive
  4. positive, negative

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: (D) positive, negative

Explanation

The gain of each controller has to make the loop a negative feedback loop. For the pressure loop, a rising pressure needs more cooling, that is a more open valve. The valve is air-to-close, so the controller output has to fall when the pressure rises. That is a reverse-acting controller, with a positive gain (the usual convention $u = K_c(SP - PV)$). For the composition loop, a rising impurity in the distillate needs more reflux, so the output (the L/D setpoint) has to rise when the impurity rises, a direct-acting controller with a negative gain. So the signs are positive for PC and negative for CC.