GATE 2018 ME (ME2) – Question 53

Thermal Engineering Applications · Refrigeration and heat pump cycles · 2 marks · Numerical answer

A standard vapour-compression refrigerator condenses at 35°C and evaporates at −10°C, providing 15 kW cooling. Its pressure–enthalpy diagram is shown. Compressor isentropic efficiency is 0.75. Find compressor power (kW), to two decimal places.

Diagram for GATE 2018 ME (ME2) question 53

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: 9.50 to 10.50

Explanation