GATE 2017 EE (EE2) – Question 55
A 25 kVA Y–delta transformer has primary line voltage 3.3 kV on the Y side and per-phase turns ratio 5:1. Its secondary line-current rating in amperes is ________.
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: 37 to 39
Explanation
The primary winding voltage is 3300/√3 V. Dividing by the phase turns ratio gives secondary winding voltage $3300/(5\sqrt3)$ V.
On the delta side winding voltage equals line voltage. Use three-phase apparent power: $I_{L2}=25000/[\sqrt3\cdot3300/(5\sqrt3)]$.
This simplifies to 25000(5)/3300=**37.8788 A**, in the official 37–39 interval.