Power Systems · Series and shunt compensation, Electric field distribution and insulators, Distribution systems · 1 mark · Multiple choice

A lossless 400 kV, three-phase 50 Hz line has inductance 1.6 mH/km/phase and capacitance 10 nF/km/phase. Sending voltage is maintained at 400 kV. When delivering 300 MW, the shunt compensation needed to maintain receiving voltage 400 kV is

  1. capacitive
  2. inductive
  3. resistive
  4. zero

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: (B) inductive

Explanation

The surge impedance is $Z_c=\sqrt{L/C}=\sqrt{1.6\times10^{-3}/10^{-8}}=400$ Ω. Surge-impedance loading is $V_{LL}^2/Z_c=(400000)^2/400=400$ MW.

The actual 300 MW is below this natural loading, so line capacitance supplies more reactive power than its series inductance consumes. Shunt reactors absorb the surplus to control receiving voltage. Compensation is **inductive, B**.