In the figure shown, self-impedances of the two transmission lines are 1.5j p.u each, and $Z_m=0.5j$ p.u is the mutual impedance. Bus voltages shown in the figure are in p.u. Given that $\delta>0$, the maximum steady-state real power that can be transferred in p.u from Bus-1 to Bus-2 is
Two coupled parallel lines carry equal currents, so each sees $Z_s+Z_m=1.5j+0.5j=2j$. The equivalent impedance is $\frac{2j}{2}=j$ p.u, and $P_{max}=\frac{|E||V|}{1}=|E||V|$.