GATE 2015 EE (EE2) – Question 16

Electrical and Electronic Measurements · Measurement of voltage, current, power, energy and power factor · 1 mark · Multiple choice

A balanced three-phase load consumes 5 kW at pf 0.707, measured by the two-wattmeter method. The readings are

  1. 3.94 kW and 1.06 kW
  2. 2.50 kW and 2.50 kW
  3. 5.00 kW and 0.00 kW
  4. 2.96 kW and 2.04 kW

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: (A) 3.94 kW and 1.06 kW

Explanation

The readings satisfy W1+W2=P=5 kW and tanφ=√3(W1−W2)/(W1+W2). With cosφ≈0.707, φ≈45° and tanφ≈1.

Thus W1−W2≈5/√3=2.88675 kW. Adding and subtracting gives W1≈3.9434 and W2≈1.0566 kW. Hence **A**; exchanging instrument labels swaps the pair without changing the answer.