GATE 2018 EE – Question 15
Two wattmeter method is used for measurement of power in a balanced three-phase load supplied from a balanced three-phase system. If one of the wattmeters reads half of the other (both positive), then the power factor of the load is
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: (D) 0.866
Explanation
For a balanced load the two-wattmeter readings are $W_1=VI\cos(30^\circ-\phi)$ and $W_2=VI\cos(30^\circ+\phi)$, and
$\tan\phi=\sqrt3\,\dfrac{W_1-W_2}{W_1+W_2}$.
With $W_1=2W_2$: $\tan\phi=\sqrt3\,\dfrac{2-1}{2+1}=\dfrac1{\sqrt3}$, so $\phi=30^\circ$ and the power factor is $\cos30^\circ=0.866$.