Consider a lossy transmission line with $V_1$ and $V_2$ as the sending and receiving end voltages, respectively. $Z$ and $X$ are the series impedance and reactance of the line, respectively. The steady-state stability limit for the transmission line will be
Correct answer: (B) less than $\left|\frac{V_1V_2}{X}\right|$
Explanation
For a lossy line the maximum power transferred at the receiving end is $\frac{|V_1V_2|}{|Z|}-\frac{|V_2|^2R}{|Z|^2}$, which is less than $\frac{|V_1V_2|}{X}$ because $|Z|>X$ and the resistance dissipates power.