GATE 2020 AG – Question 21
A cold store cools 100 metric tons of potatoes from 35°C to 8°C in five hours. Potato heat capacity is 3.1 kJ/(kg °C), refrigeration COP 3.66, and R-22 evaporation latent heat 230 kJ/kg at −10°C. Neglect respiration and losses. Find refrigerant rate and compressor power.
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: (A) 121.3 kg/min;127.1 kW
Explanation
Cooling rate is $100000(3.1)(35-8)/(5\times3600)=465$ kW. Refrigerant flow is 465/230=2.0217 kg/s=121.3 kg/min. Compressor power is 465/3.66=127.1 kW. Thus A.