GATE 2022 EE – Question 60

Power Electronics · Single-phase and three-phase voltage and current source inverters, sinusoidal pulse width modulation · 2 marks · Numerical answer

A 3-phase grid-connected voltage source converter with DC link voltage of 1000 V is switched using sinusoidal Pulse Width Modulation (PWM) technique. If the grid phase current is 10 A and the 3-phase complex power supplied by the converter is given by $(-4000-j3000)$ VA, then the modulation index used in sinusoidal PWM is ________. (round off to two decimal places)

Practise this question in The GATE Grind →

Show answer and explanation

Correct answer: 0.46 to 0.48

Explanation

The apparent power is $|S|=\sqrt{4000^2+3000^2}=5000$ VA $=3V_{ph}I_{ph}$ with $I_{ph}=10$ A rms, so $V_{ph}=166.7$ V rms. For sinusoidal PWM, $V_{ph,rms}=\frac{mV_{dc}}{2\sqrt2}$, so $m=\frac{166.7\times2\sqrt2}{1000}=0.47$.