GATE 2024 XE — all source sections – Question 95
Following data is for an actual vapour compression refrigeration cycle. Enthalpy at compressor inlet: 246kJ/kg Enthalpy at compressor exit: 286kJ/kg Heat load on the evaporator: 158kJ/kg The enthalpy at the exit of the condenser in kJ/kg is ________ (rounded off to the nearest integer).
Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: 88 to 88
Explanation
Evaporator heat per kg is h1 − h4. Thus h4 = 246 − 158 = 88 kJ/kg. The expansion valve is isenthalpic, so condenser-exit h3 = h4 = 88 kJ/kg. Compressor-exit enthalpy is not needed for this particular balance.