Write both as sines: $v=170\sin\left(377t-\frac\pi6+\pi\right)=170\sin\left(377t+\frac{5\pi}6\right)$ and $i=8\sin\left(377t+\frac\pi6+\frac\pi2\right)=8\sin\left(377t+\frac{2\pi}3\right)$. The phase difference is $\frac{5\pi}6-\frac{2\pi}3=\frac\pi6=30^\circ$, so $P=\frac12(170)(8)\cos30^\circ=588.9$ W.