In a 100 bus power system, there are 10 generators. In a particular iteration of Newton Raphson load flow technique (in polar coordinates), two of the PV buses are converted to PQ type. In this iteration,
the number of unknown voltage angles increases by two and the number of unknown voltage magnitudes increases by two.
the number of unknown voltage angles remains unchanged and the number of unknown voltage magnitudes increases by two.
the number of unknown voltage angles increases by two and the number of unknown voltage magnitudes decreases by two.
the number of unknown voltage angles remains unchanged and the number of unknown voltage magnitudes decreases by two.
Correct answer: (B) the number of unknown voltage angles remains unchanged and the number of unknown voltage magnitudes increases by two.
Explanation
At a PV bus the voltage magnitude is fixed and only the angle is unknown. At a PQ bus both the magnitude and the angle are unknown. Converting two PV buses to PQ leaves the angles unknown as before, but adds two unknown voltage magnitudes.
More Per-unit quantities, Bus admittance matrix, Gauss-Seidel and Newton-Raphson load flow methods questions
GATE 2015 EE Q52– Determine the correctness or otherwise of the following Assertion [a] and the Reason [r].…
GATE 2017 EE Q20– A 3-bus power system is shown in the figure below, where the diagonal elements of Y-bus…
GATE 2017 EE Q31– A 10-bus power system consists of four generator buses indexed as G1, G2, G3, G4 and six…
GATE 2017 EE Q50– The bus admittance matrix for a power system network is bmatrix -j39.9 & j20 & j20 \\ j20…
GATE 2014 EE (EE1) Q51– The two-bus system shown supplies load 1.0 + j0.5 pu. Find V₁ (pu) and δ₂ respectively.
GATE 2014 EE (EE2) Q25– A three-phase star load operates at 0.9 pu voltage and 0.8 lagging power factor. Base…