GATE 2015 EE – Question 54
A sustained three-phase fault occurs in the power system shown in the figure. The current and voltage phasors during the fault (on a common reference), after the natural transients have died down, are also shown. Where is the fault located?

Practise this question in The GATE Grind →
Show answer and explanation
Correct answer: (B) Location Q
Explanation
During a fault, the currents on both sides of the fault flow towards it. The phasor diagram shows the current on line Q reversed relative to the others, which points to a fault on that line at location Q. This matches the official key.