Correct answer: (C) X matches with Q and R; Y matches with P and S.
Explanation
A CT is connected in series with the line, so its primary current is the line current (R), and its secondary must never be open-circuited because the flux would rise dangerously (Q). A PT has its primary connected in parallel with the grid (P), and its secondary burden affects the primary current (S). So CT: Q and R; PT: P and S.
More Instrument transformers, Digital voltmeters and multi-meters, Phase, Time and Frequency measurement questions
GATE 2019 EE Q33– The total impedance of the secondary winding, leads, and burden of a 5 A CT is 0.01\ . If…
GATE 2018 EE Q37– A 0-1 Ampere moving iron ammeter has an internal resistance of 50 m and inductance of 0.1…
GATE 2015 EE Q33– The primary mmf is least affected by the secondary terminal conditions in a
GATE 2017 EE (EE2) Q19– A stationary closed Lissajous pattern has 3 horizontal tangencies and 2 vertical…
GATE 2017 EE (EE2) Q57– A 10½-digit timer-counter has a 100 MHz base clock. The same numerical reading occurs in…
GATE 2025 EE Q28– Instrument(s) required to synchronize an alternator to the grid is/are