Home › Previous year questions › GATE 2019 EE › Question 33GATE 2019 EE – Question 33 Electrical and Electronic Measurements · Instrument transformers, Digital voltmeters and multi-meters, Phase, Time and Frequency measurement · 1 mark · Numerical answer
The total impedance of the secondary winding, leads, and burden of a 5 A CT is $0.01\ \Omega$. If the fault current is 20 times the rated primary current of the CT, the VA output of the CT is ________.
Practise this question in The GATE Grind →
Show answer and explanation Correct answer: 100
Explanation The CT secondary carries $20\times5=100$ A during the fault. The burden dissipates (VA output) $I^2Z=100^2\times0.01=100$ VA.
More Instrument transformers, Digital voltmeters and multi-meters, Phase, Time and Frequency measurement questions GATE 2018 EE Q37 – A 0-1 Ampere moving iron ammeter has an internal resistance of 50 m and inductance of 0.1… GATE 2015 EE Q33 – The primary mmf is least affected by the secondary terminal conditions in a GATE 2017 EE (EE2) Q19 – A stationary closed Lissajous pattern has 3 horizontal tangencies and 2 vertical… GATE 2017 EE (EE2) Q57 – A 10½-digit timer-counter has a 100 MHz base clock. The same numerical reading occurs in… GATE 2025 EE Q28 – Instrument(s) required to synchronize an alternator to the grid is/are GATE 2024 EE Q23 – The table lists two instrument transformers and their features: Instrument Transformers… All Instrument transformers, Digital voltmeters and multi-meters, Phase, Time and Frequency measurement questions →