Correct answer: (A) Line charging capacitor of finite value is present in all three lines
Explanation
Each row sum of $Y_{bus}$ gives the total shunt susceptance at that bus (half line charging plus any shunt element): bus 1: $-15+10+5=0$; bus 2: $+0.5$; bus 3: $+1$. Bus 1 has zero net shunt, so no line connected to bus 1 (lines 1-2 and 1-3) can have finite charging. That makes "charging in all three lines" impossible.