The figure is a per-phase phase-shifting transformer between buses 1 and 2, with complex ratio α having nonzero real and imaginary parts. $Y_{bus}$ and $Z_{bus}$ are each 2×2 bus matrices. Which is true?
Correct answer: (D) Both matrices are unsymmetric.
Explanation
A complex tap makes the two mutual admittance terms proportional to $-1/\alpha$ and $-1/\alpha^*$, respectively. They differ for a nonreal tap, so the bus admittance matrix is not symmetric.
For an invertible matrix, a symmetric inverse would imply a symmetric original matrix. Thus a defined bus impedance matrix is also unsymmetric. This gives the official answer **D**.
**Source qualification:** taken alone with no bus reference/shunt connections, the drawn single branch has a singular two-node admittance matrix. Zbus requires an appropriate reference/network embedding; the keyed comparison assumes that it is defined.
More Per-unit quantities, Bus admittance matrix, Gauss-Seidel and Newton-Raphson load flow methods questions
GATE 2017 EE (EE2) Q35– A polar-coordinate Newton–Raphson load-flow problem has a 100×100 Jacobian and 20 PV…
GATE 2016 EE (EE2) Q24– A power system has 100 buses, including 10 generator buses. With polar-coordinate…
GATE 2026 EE Q18– Consider a power system with N buses, of which P are generator buses and the remaining Q…
GATE 2026 EE Q41– A three-phase two-winding transformer has a voltage transformation ratio V PV…
GATE 2023 EE Q28– The bus admittance (Y bus) matrix of a 3-bus power system is given below. Y…
GATE 2023 EE Q41– The three-bus power system shown in the figure has one alternator connected to bus 2 which…